试卷: LEED AP BD+C模拟题A[查看] In a mechanically ventilated office project many of the office workers will have personal printers.
The mailroom and main copy/print room will be located in two spaces on the interior of the
second floor. What must occur for the project to achieve Indoor Environmental Quality Credit,
Indoor Chemical and Pollutant Source Control? A: MERV 13 filters must be used B: The building must have a negative pressure compared to the main copy/print room C: The personal printers must be isolated behind closed doors in a sealed room D: The mailroom must have a dedicated exhaust system 参考答案: A
本题解释: Notes:
MERV 13 filters are required for Indoor Environmental Quality Credit, Indoor Chemical and
Pollutant Source Control.
High volume copy/print/fax spaces must be separated and separately exhausted from the rest of
the building. The spaces must also have doors on them.
\'The personal printers must be isolated behind closed doors in a sealed room\' is incorrect because
personal printers with low use are allowed.
\'The building must have a negative pressure compared to the main copy/print room\' is incorrect
because the copy room must have negative pressure to avoid air and contaminates exiting the
space. If the building has a negative pressure, the building will draw out the contaminates from the
copy room.
\'The mailroom must have a dedicated exhaust system\' is incorrect because only the main copy
room needs a dedicated exhaust system. |
|