- 注册时间
- 2012-6-6
- 最后登录
- 2024-12-11
- 阅读权限
- 200
- 积分
- 5674
- 精华
- 3
- 帖子
- 1765
|
试卷: LEED AP ID+C 模拟试卷D[查看] A non-residential project does not allow smoking in the building. What must be done to achieve Environmental Tobacco Smoke Control? A: Install impermeable deck-to-deck partitions between floors B: Locate all smoking areas 25 feet from outdoor air intakes C: Directly exhaust any janitorial rooms to the outdoors D: Seal penetrations in walls between units 参考答案: B
本题解释: Notes:
See Indoor Environmental Quality Prerequisite, Environmental Tobacco Smoke (ETS) Control, Requirements
This question asks about non residential buildings.
Non-residential projects require:
No smoking inside, limited to 25 ft. of entries, outdoor air intakes and operable windows
OR
-Designated smoking rooms with dedicated exhaust systems, deck to deck partitions, and operating at a negative pressure of at least an average of 5 Pa with a minimum of 1 Pa when the doors are closed.
-Verify the differential pressure of the smoking room by conducting 15 minutes of measurement, with a minimum of 1 measurement every 10 seconds
Multi-unit residential units require:
-Sealing penetrations
-Weather stripping doors to common hallways
-Blower door test for sealing
-Demonstrate less than 1.25 square inches of leakage / 100 square feet of enclosure area, using the HERS methodology
|
|