LEED GAP

 找回密码
 立即注册

QQ登录

只需一步,快速开始

搜索
查看: 274|回复: 0
打印 上一主题 下一主题

A mechanically ventilated project space has the following zones and ventilation

[复制链接]

1759

主题

1

好友

5674

积分

管理员

Rank: 9Rank: 9Rank: 9

跳转到指定楼层
楼主
发表于 2012-8-4 18:33:34 |只看该作者 |倒序浏览
试卷: LEED AP ID+C 模拟试卷D[查看]
A mechanically ventilated project space has the following zones and ventilation rates:

Area(sf):Office 8,000 ;Conference room 750 ;Reception area 400 .
Standard airflow:Office 0.088;Conference room 0.380 ;Reception area 0.530,
Design Airflow:Office 0.120;Conference room 0.450; Reception area 0.722.

What is true about this projects ability to earn Indoor Environmental Quality Credit, Increased Ventilation?
A: The conference room can be excluded from the calculations and the project will earn the credit
B: All spaces have achieved the 30% requirements for increased ventilation
C: The credit cannot be achieved because the conference room air flow has not met the 30% requirement
D: The average ventilation rate of the spaces based on their areas is enough to achieve the credit

参考答案: C

本题解释:
Notes:

Reference: Indoor Environmental Quality Credit, Increased Ventilation, Calculations

For this credit the ventilation must increase by 30% to ALL occupied spaces. The rates cannot be averaged. First check the percent increase for each space:

Office: (1 - (0.120 / 0.088)) X 100 = 36% increase

Conference room: (1 - (0.450 / 0.380)) X 100 = 18% increase

Reception area: (1 - (0.722 / 0.530)) X 100 = 36% increase

The conference room does not have enough ventilation so the credit cannot be achieved unless the air flow is increased to meet the 30% threshold.
分享到: QQ空间QQ空间 腾讯微博腾讯微博 腾讯朋友腾讯朋友
分享分享0 收藏收藏0
回复

使用道具 举报

您需要登录后才可以回帖 登录 | 立即注册

关闭

站长推荐上一条 /1 下一条

Archiver|手机版|LEED GA/LEED AP考试学习平台|版权所有|备案号(沪ICP备11019119号-2)|leedgap   

GMT+8, 2024-12-24 00:09 , Processed in 0.075282 second(s), 25 queries .

Powered by Discuz! X2.5 & Exam 1.4

© 2001-2012 Comsenz Inc.

回顶部