试卷: LEED AP ID+C 模拟试卷D[查看] A project will have space control devices in each area enclosed by ceiling-height partitions. The tenant space will have the following rooms:
Room 1: 520 sf
Room 2: 480 sf
Room 3: 3,300 sf
Room 4: 11,432 sf
How many controls are needed to meet the lighting requirements of ASHRAE 90.1-2007?
A: 5 B: 6 C: 7 D: 4 参考答案: B
本题解释: Notes:
Energy and Atmosphere Prerequisite, Minimum Energy Performance, Implementation, Section 9
Rooms smaller than 10,000 sf must have 1 control for every 2,500 sf
Rooms larger than 10,000 sf must have 1 control for every 10,000 sf, so if the room is 50,000SF there must be 5 controls.
Room 1: 520 sf - 1 control
Room 2: 480 sf - 1 control
Room 3: 3,300 sf - 2 controls (<10,000 sf = 1 for every 2,500 sf)
Room 4: 11,432 sf - 2 controls (>10,000 sf = 1 for every 10,000 sf) |
|