试卷: LEED AP ID+C 模拟试卷D[查看] The total area for a dentist’s office 18,522 sf. The gross lighting floor area for a dentist’s office is 18,340 sf. The lighting power density for the space is 1.1 watts/sf. What amount of the connected lighting load requires occupancy sensors to earn 1 point for Energy and Atmosphere Credit, Optimize Energy Performance-Lighting Controls? A: 13,892 watts B: 15,281 watts C: 15,131 watts D: 13,755 watts 参考答案: C
本题解释: Notes:
Reference: Energy and Atmosphere Credit, Optimize Energy Performance-Lighting Power, Calculations
For the building area method use this equation:
Gross lighting floor area (sf) X Building area type lighting power density (watts/sf) = Installed interior lighting power allowances (watts)
18,340 sf X 1.1 watts/sf = 20,174 watts
To earn 1 point for occupancy sensors at least 75% of the connected lighting load must have occupancy sensors.
20,174 X 0.75 = 15,131 watts |
|