试卷: LEED AP ID+C 模拟试卷B[查看] A multi-use building includes both office space and several restaurants that permit smoking. What must be done to achieve Environmental Tobacco Smoke Control?(choose 3)
A: Weather stripping doors to common hallways B: Directly exhaust the restaurants to the outdoors C: Demonstrate the restaurants have less than 1.25 square inches of leakage / 100 square feet of enclosure area, using the HERS D: Enclose the restaurants with impermeable deck-to-deck partitions E: Verify the differential pressure of the smoking room by conducting 15 minutes of measurement, with a minimum of 1 measurement 参考答案: BDE
本题解释: See Indoor Environmental Quality Prerequisite, Environmental Tobacco Smoke (ETS) Control, Requirements
This question asks about non residential buildings.
Non-residential projects require:
No smoking inside, limited to 25 ft. of entries, outdoor air intakes and operable windows
OR
-Designated smoking rooms with dedicated exhaust systems, deck to deck partitions, and operating at a negative pressure of at least an average of 5 Pa with a minimum of 1 Pa when the doors are closed.
-Verify the differential pressure of the smoking room by conducting 15 minutes of measurement, with a minimum of 1 measurement every 10 seconds
Multi-unit residential units require:
-Sealing penetrations
-Weather stripping doors to common hallways
-Blower door test for sealing
-Demonstrate less than 1.25 square inches of leakage / 100 square feet of enclosure area, using the HERS methodology
|
|