试卷: LEED v4 ID+C模拟题B卷英文[查看] A flush-out will happen where occupancy of the building will occur before flush-out is
complete. What quantity of outside air must be introduced to the project space per sq. ft.
of floor area? A: 12,000 cu. ft. B: 14,000 cu. ft. C: 3,500 cu. ft. D: 7,000 cu. ft. 参考答案: B
本题解释: Notes:
Reference: Indoor Environmental Quality Credit, Construction Indoor Air Quality
Management Plan-Before Occupancy, Requirements
If occupancy is desired prior to completion of a flush-out a minimum of 3,500 cubic feet of
outdoor air per foot of floor area must be delivered before the space can be occupied.
These conditions must be maintained until a total of 14,000 cubic feet / sq. ft. of outside air
has been delivered to the space. |
|